Alterations and Additions in Domestic and Similar Premises

ED

ALTERATIONS AND ADDITIONS IN DOMESTIC AND SIMILAR PREMISES

 

EDQ1

Do socket-outlets added to an existing installation in domestic premises have to be RCD-protected?

 

EDA1

Where socket-outlets are added to an existing circuit that is not already RCD-protected, either the circuit will need to have RCD protection added, or the new socket-outlets must incorporate RCD protection (except for a socket-outlet designated for a particular item of equipment, such as a freezer). However, refer also to EDQ3 and EDA3.

 

411.3.3

EDQ2

When an electrical appliance such as a boiler or electric towel rail is to be installed in a bathroom where there is no supplementary bonding, and the consumer unit has rewireable fuses and no RCD protection, how can the installer comply with the 17th Edition?

 

EDA2

If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.

 

701.411.3.3
701.415.2

EDQ3

A socket-outlet is to be added to an existing circuit. The work is not being carried out in a special location and the existing circuit has no RCD protection. The new socket-outlet is to be flush mounted 150 mm horizontally from an existing socket-outlet, and connected with wiring concealed in the wall. What is reasonably expected for the installer to do to comply with the 17th Edition?

 

EDA3

A socket-outlet that is added to an existing circuit will need to have RCD protection (except for a socket-outlet designated for a particular item of equipment, such as a freezer).
In addition, if the wiring that is used to extend the existing circuit is concealed in the wall, then at least the extended part of the existing circuit will need to be suitably protected (by RCD or other means).

 

411.3.3
522.6.6 to 522.6.8

 

EDQ4

A switched, fused 13 A connection unit is to be added to an existing circuit. The work is not being carried out in a special location and the existing circuit has no RCD protection. The incoming services are bonded and the new switched fused connection unit is to be flush mounted 150 mm horizontally from an existing socket, and connected with wiring concealed in the wall. What is the reasonably expected for the installer to do to comply with the 17th Edition?

 

EDA4

The connection unit does not require additional protection by RCD, though at least the extended part of the existing circuit will need to be suitably protected (by RCD or other means).

 

522.6.6 to 522.6.8

EDQ5

Can I carry out an alteration or addition to an existing installation that has inadequate earthing and/or bonding arrangements?

 

EDA5

Yes, but regardless of the extent of the work, the alteration or addition, on completion, must comply with the current edition of BS 7671. This requires that the earthing and bonding arrangements upon which the new work relies for safety are adequate.

 

131.8 

EDQ6

With the increased requirement for circuits in domestic premises to be RCD-protected, it may be necessary for the smoke detector to be connected to an RCD-protected circuit, which may not be acceptable to the client. How could this issue be addressed without surface wiring?

 

EDA6

For smoke detectors having an integral standby supply (battery or capacitor), connection to an RCD-protected circuit is permitted by BS 5839-6.

 

 

 

EDQ7

When changing a consumer unit, do I need to provide RCDs for all circuits required by the 17th Edition to have additional protection, such as socket-outlets, bathroom circuits and cable concealed in walls and partitions?

 

EDA7

Yes. There should be more than one RCD, and the circuits should be divided between them in order to minimize the likelihood and consequences of tripping.

 

314.1

EDQ8

If an existing socket-outlet not having additional protection by RCD needs to be replaced, does such additional protection need to be provided for the replacement socket?

 

EDA8

No. Such maintenance or repair work would not be classified as an alteration or addition.

 

411.3.3

EDQ9

I need to replace a length of damaged cable in a circuit that is not RCD-protected. The 17th Edition would require a new circuit following the same route to have additional protection by means of an RCD. Do I have to provide such protection for the repaired circuit?

 

EDA9

No. Such repair work would not be classified as an alteration or addition.

 

411.3.3

EDQ10

If I replace an existing electric shower, do I now have to provide RCD protection for it?

 

EDA10

No, unless RCD protection is required by the manufacturer’s installation instructions, or a new circuit is required (to provide for increased load, for example).

 

 

134.1.1 510.2

EDQ11

When installing a non-electrical radiator in an existing bathroom, does the 17th Edition require it to be supplementary bonded?

 

EDA11

Supplementary bonding would be required for any new extraneous-conductive-part installed in a bathroom or shower room unless all the other requirements of Regulation 701.415.2 have been met.

 

701.415.2

EDQ12

When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?

 

EDA12

Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.

 

701.415.2


 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

 

..............................................................................................................................................................................