Alterations and Additions in Domestic and Similar Premises topics

Alterations and Additions in Domestic and Similar Premises

ED

ALTERATIONS AND ADDITIONS IN DOMESTIC AND SIMILAR PREMISES

 

EDQ1

Do socket-outlets added to an existing installation in domestic premises have to be RCD-protected?

 

EDA1

Where socket-outlets are added to an existing circuit that is not already RCD-protected, either the circuit will need to have RCD protection added, or the new socket-outlets must incorporate RCD protection (except for a socket-outlet designated for a particular item of equipment, such as a freezer). However, refer also to EDQ3 and EDA3.

 

411.3.3

EDQ2

When an electrical appliance such as a boiler or electric towel rail is to be installed in a bathroom where there is no supplementary bonding, and the consumer unit has rewireable fuses and no RCD protection, how can the installer comply with the 17th Edition?

 

EDA2

If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.

 

701.411.3.3
701.415.2

EDQ3

A socket-outlet is to be added to an existing circuit. The work is not being carried out in a special location and the existing circuit has no RCD protection. The new socket-outlet is to be flush mounted 150 mm horizontally from an existing socket-outlet, and connected with wiring concealed in the wall. What is reasonably expected for the installer to do to comply with the 17th Edition?

 

EDA3

A socket-outlet that is added to an existing circuit will need to have RCD protection (except for a socket-outlet designated for a particular item of equipment, such as a freezer).
In addition, if the wiring that is used to extend the existing circuit is concealed in the wall, then at least the extended part of the existing circuit will need to be suitably protected (by RCD or other means).

 

411.3.3
522.6.6 to 522.6.8

 

EDQ4

A switched, fused 13 A connection unit is to be added to an existing circuit. The work is not being carried out in a special location and the existing circuit has no RCD protection. The incoming services are bonded and the new switched fused connection unit is to be flush mounted 150 mm horizontally from an existing socket, and connected with wiring concealed in the wall. What is the reasonably expected for the installer to do to comply with the 17th Edition?

 

EDA4

The connection unit does not require additional protection by RCD, though at least the extended part of the existing circuit will need to be suitably protected (by RCD or other means).

 

522.6.6 to 522.6.8

EDQ5

Can I carry out an alteration or addition to an existing installation that has inadequate earthing and/or bonding arrangements?

 

EDA5

No. Any alteration or addition to an existing installation must comply with the current edition of BS 7671 (including any amendments). This requires any earthing and bonding arrangements upon which the alteration or addition relies for safety to be adequate. Any exposed-conductive-parts of the new work must not be simultaneously accessible with exposed-conductive-parts of the existing installation that are not connected to the same earthing system.

 

131.8 
633.2
411.3.1.1

EDQ6

How can I avoid providing RCD protection for a new socket-outlet intended to supply a particular item of equipment for use indoors, such as a fridge or freezer, when cables concealed in a wall or partition, and socket-outlets, are generally required to be RCD protected?

 

EDA6

Cables concealed in a wall or partition are not required to be RCD protected if they are installed in accordance with Regulation 522.6.6 (i), (ii), (iii) or (iv), or Regulation 522.6.8 (i), (ii), (iii) or (iv), as applicable. This includes cables having an earthed metallic covering or earthed metallic enclosure meeting the specified requirements.

The socket-outlet would need to be specifically labelled or otherwise suitably identified for connection of the particular item of equipment

 

522.6.6

522.6.8

411.3.3

EDQ7

When changing a consumer unit, do I need to provide RCDs for all circuits required by the 17th Edition to have additional protection, such as socket-outlets, bathroom circuits and cable concealed in walls and partitions?

 

EDA7

Yes. There should be more than one RCD, and the circuits should be divided between them in order to minimize the likelihood and consequences of tripping.

 

314.1

EDQ8

If an existing socket-outlet not having additional protection by RCD needs to be replaced, does such additional protection need to be provided for the replacement socket?

 

EDA8

No. Such maintenance or repair work would not be classified as an alteration or addition.

 

411.3.3

EDQ9

I need to replace a length of damaged cable in a circuit that is not RCD-protected. The 17th Edition would require a new circuit following the same route to have additional protection by means of an RCD. Do I have to provide such protection for the repaired circuit?

 

EDA9

No. Such repair work would not be classified as an alteration or addition.

 

411.3.3

EDQ10

If I replace an existing electric shower, do I now have to provide RCD protection for it?

 

EDA10

No, unless RCD protection is required by the manufacturer’s installation instructions, or a new circuit is required (to provide for increased load, for example).

 

 

134.1.1 510.2

EDQ11

When installing a non-electrical radiator in an existing bathroom, does the 17th Edition require it to be supplementary bonded?

 

EDA11

Supplementary bonding would be required for any new extraneous-conductive-part installed in a bathroom or shower room unless all the other requirements of Regulation 701.415.2 have been met.

 

701.415.2

EDQ12

When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?

 

EDA12

Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.

 

131.8
544.1.1

EDQ13

If a dwelling has an existing consumer unit with an integral main switch, and an electric shower is connected by means of a second consumer unit with an integral main switch, is another ‘main switch’ required to isolate both consumer units simultaneously?

 

EDA13

Regulation 537.1.4 requires a main linked switch or linked circuit-breaker to be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

However, it is permitted for a dwelling to have more than one electrical installation. Therefore a further ‘main switch’ is not required to isolate both consumer units.

Regulation 537.2.2.6 requires each device used for isolation to be clearly identified by position or durable marking to indicate the installation it isolates.

 

537.1.4

EDQ14

When carrying out an alteration or addition to an existing installation protected by a voltage-operated earth-leakage circuit-breaker, can that device be used to provide electric shock protection for the new work?

 

EDA14

No. As the new work must comply with BS 7671, fault protection must be provided by an overcurrent device or RCD, and additional protection, where required (such as for socket-outlets or cables concealed in walls), must be provided by a 30 mA RCD.

 

 

EDQ15

If I replace a distribution board which feeds a number of sub-distribution boards, am I responsible for testing the outgoing circuits of the sub-distribution boards?

 

EDA15

No.

 

EDQ16

If we reposition a pull switch in a location containing a bath or shower, would the circuit need to be RCD-protected?

 

EDA16

Yes, because the work would be more than just a like-for-like replacement.

701.411.3.3

EDQ17

Is BS 8436 cable resistant to damage by rodents?

 

EDA17

No, not without additional mechanical protection.

 

EDQ18

What should I do if a consumer unit I have been asked to replace is in a relatively inaccessible position?

 

EDA18

You should make your customer aware of the issues relating to accessibility, including the need to test RCDs at quarterly intervals, to enable the customer to make an informed decision about the position of the replacement consumer unit.

513.1


 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

 

..............................................................................................................................................................................