HOME
 









Electrical Safety Council
New or rewired domestic and similar installations back

New or Rewired Domestic and Similar Installations

ND

NEW OR REWIRED DOMESTIC AND SIMILAR INSTALLATIONS

 

NDQ1

Does the 17th Edition require all 13 A socket-outlets in domestic premises to be RCD-protected?

 

NDA1

For new installations and rewires in domestic premises, all socket-outlets need to have additional protection by RCD, except perhaps for those intended to supply particular items of equipment such as freezers. Any socket-outlet not having RCD protection needs to be specifically labelled or otherwise suitably identified to indicate its intended use, such as ‘freezer only’. However, if the wiring to a dedicated socket-outlet is concealed in a wall or partition at a depth of less than 50 mm, or if the internal construction of the wall or partition includes metallic parts other than metallic fixings, the circuit will still need to be suitably protected (by RCD or other means).

411.3.3

522.6.6
522.6.8

 

NDQ2

The 17th Edition requires most if not all circuits in domestic premises to be RCD-protected. There have been a number of suggestions as to how the consumer unit may best be configured to comply with the Regulations, the most common being a main switch with RCBOs protecting each individual circuit. However, another suggestion favours a main switch with two RCDs protecting separate DIN rails. If careful consideration is given as to what each bar will control in the way of upstairs and downstairs lighting and power circuits, will this configuration comply?

 

NDA2

Yes, as long as the division of final circuits between the RCDs is carefully considered so as to minimize the consequences of unwanted tripping. Separate RCD protection is not necessarily required for each circuit of an installation but, in order to minimize the likelihood and consequences of tripping, a single (‘front end’) RCD should not be used to protect all the circuits.

 

314.1

NDQ3

The 17th Edition does not now define a zone 3 in a bathroom or shower room. What electrical equipment and accessories can be installed in the area between 0.6 m and 3.0 m from the edge of the bath or shower basin? Moreover, what minimum degree of IP protection are manufacturers likely to recommend?

 

NDA3

There is no change from the 16th Edition requirements – that is, the general rules apply.  The manufacturer’s installation instructions must always be followed.

 

512.2
134.1.1

 

NDQ4

Do ‘meter tails’ concealed in walls or partitions need to be protected in accordance with Regulations 522.6.6 and/or 522.6.8?

 

NDA4

Yes. Meter tails concealed in a wall or partition at a depth of less than 50 mm from a surface must be protected in accordance with Regulation 522.6.6. Also, irrespective of the depth from a surface, meter tails concealed in a wall or partition having internal metallic parts (except nails and screws, etc) are subject to the requirements of Regulation 522.6.8.

However, additional protection for meter tails by means of an RCD is not an acceptable option in respect of Regulation 522.6.7 (which in consequence rules out reliance on 522.6.6(v), routing in the ‘safe zones’ alone), or in respect of Regulation 522.6.8(v). Also, for TT systems, the only option remaining is to provide suitable mechanical protection (that is, to comply with Regulations 522.6.8(iv) and/or 522.6.6(iv) as appropriate).

 

522.6.6, 522.6.8
314.1, 314.2

NDQ5

Where the Regulations specify additional protection by RCD, does this include RCBOs?

 

NDA5

Yes. Where the generic term ‘RCD’ is used, it refers to most types of residual current device including RCBOs (Residual current-operated circuit-breakers with integral overcurrent protection), RCCBs (Residual current-operated circuit-breakers without integral overcurrent protection) and SRCDs (Socket-outlets incorporating a residual current device). For the purposes of the Regulations, it does not include PRCDs (Portable residual current devices).

 

411.3.3

NDQ6

Does boiler pipework need to have additional equipotential bonding for electrical safety reasons?

 

NDA6

There is no specific requirement in the Regulations for boiler pipework to be supplementary bonded. However, such bonding may be called for in the boiler manufacturer’s instructions, in which case BS 7671 requires those instructions to be followed (Regulation 510.2 refers). Any stated requirement for additional bonding that is considered to be unnecessary should be queried with the manufacturer concerned, and amended installation instructions requested.

 

411.3.3

NDQ7

Does the dispensation in Regulation 701.415.2 to omit supplementary bonding in a location containing a bath or shower apply to TT systems?

 

NDA7

Yes

 

701.415.2

NDQ8

If the mains supply cable to a fixed appliance such as a flat screen TV is concealed in a wall or partition at a depth of less than 50 mm, does the 17th Edition require the lead to be RCD-protected in accordance with Regulation 522.6.7 even though it’s connected by means of a plug and socket?

 

NDA8

Yes. The risk of penetration by a nail or screw is the same as for other concealed cable. Also, if the wall or partition has internal metallic parts (except nails and screws, etc), RCD protection in accordance with Regulation 522.6.8 is required irrespective of the depth of the cable from the surfaces.

 

522.6.7, 522.6.8

NDQ9

To overcome thermal insulation issues, is it permissible to design a ring final circuit using 2.5 mm² cable protected by a 20 A protective device?

 

NDA9

Yes, if the effective current carrying capacity of the cable is at least 12.5 A (20 A × 20/32), so as to effectively have the same ‘deemed to comply status’ as Regulation 433.1.5 gives to 30 A and 32 A ring final circuits.

 

433.1.5

NDQ10

Should signal amplifiers mounted at high level on television aerials where they might be struck by lightning be main bonded?

 

NDA10

There is no specific requirement in BS 7671 but, if there is considered to be a significant risk of a lightning strike, the advice of a lightning protection specialist should be sought.

 

 

NDQ11

I am still working on an electrical installation that was designed to the 16th Edition. To which Edition should the installation be inspected, tested, verified and certificated?

 

NDA11

An installation designed and installed to the 16th Edition should be inspected, tested, verified and certificated to that Edition.

 

 

NDQ12

What types of mechanical protection provide sufficient protection against penetration by nails, screws and the like?

 

NDA12

As an example, steel of 3 mm minimum thickness is generally considered to provide sufficient mechanical protection, except where shot-fired nails are likely to be used.

522.6.6
522.6.8

 

NDQ13

Five flats are fed individually from five ‘sub-mains’ originating at the main intake position. The five gas and water meters are main bonded at the main intake position. Do we still need to provide main bonding in each of the flats?

 

NDA13

Whilst main protective bonding is required at the main intake position, it is good practice also to provide main protective bonding in each flat even though, in this case, the origin of each installation could be considered to be at the main intake position.

 

411.3.1.2

NDQ14

Is an RCD main switch (such as a 100 mA time-delayed device) still required in the consumer unit of a new domestic installation forming part of a TT system?

 

NDA14

For a domestic installation complying with the 17th Edition where all the final circuits are RCD-protected, an RCD main switch is no longer required, provided that the consumer unit is of all insulated construction.

 

 

NDQ15

Does the device that has to be provided for switching off a bathroom extract fan for mechanical maintenance need to be located adjacent to the fan?

 

NDA15

No, but the device does need to be so placed and marked as to be readily identifiable and convenient for the intended use

 

537.3.2.4

NDQ16

Can accessories and electrical equipment such as socket-outlets and under-cupboard lighting be fixed to fitted kitchen units?

530.4.2 

NDA16

Yes, provided that they are securely fixed to rigid parts of the units that are not demountable or otherwise liable to be disturbed in normal service. However, care must be taken to comply with all the relevant requirements of BS 7671, including accessibility for inspection, testing and maintenance, and provision of adequate protection against damage (by impact or water for example) for the accessories, equipment and associated wiring. Regulation 530.4.2 is not intended to preclude such common practice. This is intended to be clarified in the 17th Edition in due course.

 

 

NDQ17

When a Grade D fire detection and alarm system to BS 5839-6: 2004 is protected by an RCD, should the RCD operate independently of any circuits supplying socket-outlets or portable equipment?

 

NDA17

There are no particular requirements or limitations in BS 5839-6 concerning the use of RCDs with Grade D fire detection and alarm systems.

For Grade D systems, which comprise one or more mains-powered smoke alarms each with an integral standby power (such as typical domestic smoke alarm with battery), BS 5839-6 simply recommends that the mains supply to the smoke and/or heat alarms should take the form of either:
i) an independent circuit at the dwelling’s main distribution board, in which case no other electrical equipment should be connected to the circuit (other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke and/or heat alarms), or
ii) a separately electrically protected, regularly used local lighting circuit.

We recommend option ii) on the grounds that disconnection of the supply to the fire detection and alarm system will be more readily noticed. In our opinion ‘separately electrically protected’ does not preclude sharing an RCD with several other circuits where this is permitted by BS 7671.

 

 

NDQ18

Does the 17th Edition permit connection of smoke alarms to an adjacent lighting circuit taking into account Regulation 560.7.1, which states that circuits of safety services shall be independent of other circuits?

 

NDA18

Yes. The particular requirements of BS 5839-6 take precedence over the general requirements of BS 7671.

 

110.1 

NDQ19

Does the R1 + R2 test confirm& the correct polarity of a radial circuit?

 

NDA19

No, not on its own. Whilst the test can provide an indication of polarity, it needs to be combined with inspection and further testing as required by Part 6 of BS 7671: 2008

 

611.3, 612.6

NDQ20

Appendix 15 of BS 7671: 2008 gives advice on ring final circuits and sharing/spreading the load around the circuit. Item (iii) suggests that cookers, ovens and hobs over 2 kW should be on their own dedicated circuit. Why can’t ovens of less than 3 kW be connected to a ring final circuit via a suitable connection point such as a socket-outlet or fused connection unit?

 

NDA20

Appendix 15 is intended to give guidance only. Such connection is not prohibited, provided that no part of the ring final circuit will be overloaded as a result.

 

433.1.5

NDQ21

Are Regulations 522.6.6, 522.6.7 and 522.6.8, which require additional protective measures for cables concealed in walls and partitions, intended to apply to cables of SELV, PELV, FELV and/or Reduced Low Voltage systems (other than to the cables supplying the sources at Low Voltage)?

 

NDA21

No. This is intended to be clarified in the 17th Edition in due course.

 

 

NDQ22

In locations containing a bath or shower, is Regulation 701.411.3.3, which requires additional protection by RCD, intended to apply to circuits of SELV, PELV, FELV and/or Reduced Low Voltage systems (other than to the cables supplying the sources at Low Voltage if installed within the location)?

 

NDA22

No. This is intended to be clarified in the 17th Edition in due course.

 

 

NDQ23

In ‘smith construction’ or ‘truss’ dwellings, metal frame parts in the loft area are likely to be bolted to structural metalwork embedded in the ground and hence are likely to be extraneous-conductive-parts. Do they require main protective bonding?

 

NDA23

If the metallic structure falls within the definition of an extraneous-conductive-part given in Part 2 of BS 7671, it is required to be main bonded.

 

411.3.1.2

NDQ24

Do circuits supplying extra-low voltage lighting in a bathroom or shower room need RCD protection?

 

NDA24

RCD protection is not required for SELV or PELV circuits. However, RCD protection is likely to be required for the circuits supplying such sources, such as to comply with Regulation 522.6.7 (See also other Q&As)

 

 

NDQ25

Is it necessary to verify voltage drop during initial verification?

 

NDA25

Verification of voltage drop is not normally required unless there is considered to be a voltage drop problem.

 

612.14

NDQ26

Considering Regulations 134.1.1 and 510.2 which require equipment to be installed in accordance with instructions provided by the manufacturer, are installers now required to check torque settings for connection tightness at consumer units where these are manufacturers instructions.

 

NDA26

Yes. It is necessary to check that all connections are tight, and any specific installation instructions must also be followed.

 

 

NDQ27

In a location containing a shower, what is the horizontal limit of zone 1 for showers without a basin?

 

NDA27

The limit of zone 1 horizontally is 1.2 m from the centre point of the fixed water outlet (the end of the rigid pipe of the fixed water installation) on the wall or ceiling, irrespective of whether the shower head is fixed or on the end of a flexible hose. Beyond zone 1, the general rules of BS 7671 apply, including Regulation 512.2 concerning external influences. In particular, the IP rating of any electrical equipment must be adequate.

 

701.32.4

512.2

NDQ28

Regulation 560.7.7 requires cables for safety circuits, other than metallic screened fire-resistant cables, to be adequately and reliably separated from other circuit cables. In addition to mineral insulated cables, what cables would be exempted from this separation requirement?

560.7.7

NDA28

Soft-skinned cables to BS 7629-1: 2008 would be exempted from the separation requirements as they have a metallic screen and their survival in a fire has been tested in accordance with BS EN 50200. However, cables to BS 8436: 2004 would not be exempted as the product standard does not require their fire resistance to be tested. Irrespective of the above, BS 5839-1 recommends that, for a fire detection and alarm system complying with that standard, the circuits of fire alarm systems should be segregated from the cables of other circuits to minimize the potential for those other circuits to cause malfunction of the fire alarm system.

 

 

NDQ29

Is it acceptable to use an unfixed connector block to join the line or neutral conductors at a light switch?

 

NDA29

Yes.

 

 

NDQ30

As the designer of an installation, am I allowed to rely on the RCD element of an RCBO to provide for fault protection in order to allow for loop impedance values greater than given in Table 41.3?

 

NDA30

Yes, so long as all the other applicable requirements of the 17th Edition are met, including those for protection against overload and short circuit.

 

411.4.4
411.4.5
411.4.9

NDQ31

Are there any particular requirements relating to the mounting height or location of consumer units for electrical installations in new dwellings?

 

NDA31

The provision of access to consumer units is not specifically covered by Building Regulations or BS 7671. However, consumer units need to be so located as to enable reasonable access to the users, including for the purpose of testing the RCDs at regular intervals, and in case of emergency.

 

132.12
341.1
513.1

NDQ32

Is the space within an airing cupboard in a bathroom or shower room that would otherwise be in a particular zone were it not for the cupboard door, considered to be within that zone?

 

NDA32

No, unless the cupboard door does not effectively limit the extent of the location. However, where an airing cupboard opens into zone 1 or zone 2, we recommend that circuits supplying equipment in the airing cupboard are be provided with additional protection in accordance with Regulation 415.1.1.

 

701.32.1
701.411.3.3

 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

..............................................................................................................................................................................
© ESC 2008