PERIODIC INSPECTION OF EXISTING DOMESTIC AND SIMILAR INSTALLATIONS

 

PDQ1

During periodic inspections of domestic electrical installations, I often find that cables that are concealed in walls at a depth of less than 50 mm have no additional protection by means of an RCD, as is now required for installations complying with the 17th Edition. What Recommendation Code should I give?

 

PDA1

Code 4. Although existing installations need to be assessed against the requirements of the 17th Edition, this does not necessarily mean that they require upgrading, unless a departure from the latest requirements constitutes an immediate or potential danger.

 

Introduction to
BS 7671: 2008

PDQ2

Where can I find the limiting values of measured earth fault loop impedance for BS 3871 circuit breakers?

 

PDA2

Click here!

 

PDQ3

What Recommendation Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?

 

PDA3

Recommendation Code 2

 

PDQ4

Is it necessary to verify voltage drop during a periodic inspection?

 

PDA4

Verification of voltage drop is not normally required unless there is considered to be a voltage drop problem.

 

621.2

PDQ5

Where can I find general guidance on the use of Recommendation Codes for domestic periodic inspection reports?

 

PDA5

General guidance on the use of Recommendation Codes is available in the Electrical Safety Council’s Best Practice Guide No 4, which may be viewed or downloaded free of charge by clicking here

 

PDQ7

What should be recommended if, during a periodic inspection, the safety of an installation forming part of a TT system is found to be relying on a voltage-operated earth-leakage circuit-breaker (VOELCB) for fault protection?

 

PDA7

If a VOELCB on a TT system fails to operate when tested with an instrument or integral test button, this would normally warrant a Code 1 recommendation (requires urgent attention).

But, subject to the VOELCB being proved to operate correctly, continued reliance on it for fault protection (protection against indirect contact) would normally warrant a Code 4 recommendation.

However, if the VOELCB relies on a water pipe not permitted by Regulation 542.2.4 to be a means of earthing, this should attract a Code 2 recommendation (requires improvement).

 

PDQ8

What should I recommend in a periodic inspection report if I find that an existing installation still relies for fault protection on a voltage-operated earth-leakage circuit-breaker?

 

PDA8

If the device fails to trip when the integral test button is operated, the device should be replaced with RCD protection as a matter of urgency (Recommendation Code 1).

If the device trips on operation of the test button, it may remain in service (Recommendation Code 4).

However, the user should be given clear instructions to test the device at quarterly intervals by means of the integral test button.

The user should also be advised that the voltage-operated device should be replaced with RCD protection at the earliest opportunity to enhance the safety of the installation.

PDQ9

In an existing domestic installation, are 16 mm2 single-core pvc/pvc meter tails (having a current-carrying capacity of 87 A clipped direct) adequate if the rating of the distributor’s BS 1361 cut-out fuse is 100 A?

 

PDA9

This size of tails may be adequate provided the maximum demand of the installation, taking into account the load characteristics (diversity and load profile), does not exceed the current-carrying capacity of the tails, and also provided that the requirements of Regulation 434.5.2 for protection of the tails against fault current are met.

As a practical tip, the current-carrying capacity of the meter tails is likely to be adequate if they have been in service for several years and there are no signs of thermal damage at the terminations or to the cable sheath or insulation.

311.1
433.3.1(ii)
434.5.2

PDQ10

In an existing domestic installation, is a 10 mm2 or 6 mm2 earthing conductor adequate if the rating of the distributor’s BS 1361 cut-out fuse is 100 A?

 

PDA10

This size of earthing conductor will be adequate if the requirements of Regulation 543.1.3 (adiabatic equation) are met.

However, if the supply is PME, the earthing conductor is usually required to be at least 10 mm2
(but see EDQ12 and EDA12)

543.1.3
542.3.1
544.1.1

PDQ11

What is the correct sequence for testing RCDs?

 

PDA11

Preferably, RCDs should be tested in the sequence of: x1I?n, x5I?n (if required for additional protection), followed by x0.5 I?n and then finally the test button trip.

However, some automated test instruments test in the sequence of: x0.5 I?n followed by the x1I?n test, and then x5I?n test (if required for additional protection).

In any case, the test button should be operated last in the test sequence.

 


 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

 

..............................................................................................................................................................................