HOME
 









ESC shop

ESC shop

WN

PLACES OF WORK – NEW INSTALLATIONS

 

WNQ1

The 17th Edition requires socket-outlets rated at up to 20 A and intended for use by ordinary persons to be provided with additional protection by means of a 30 mA RCD. Many socket-outlets in offices may be considered to be subject to this requirement. However, many offices will have computers producing protective conductor current, individually and/or collectively. This accumulated protective conductor current could cause the circuit RCD to operate. Such disruption will not be acceptable to the office users, particularly in banks etc. How can such unwanted tripping be avoided?

 

WNA1

Where additional protection by RCD is necessary, unwanted tripping can be avoided by appropriate sub-division of circuits.

 

314.1, 531.2.4.

WNQ2

Which 13 A socket-outlets in commercial and industrial premises are required to have additional protection by RCD?

 

WNA2

Socket-outlets in commercial and industrial premises must have additional protection by means of an RCD if they are rated at 20 A or less and are for general use without the supervision of a skilled or instructed person.  An exception is made for a specific labelled/identified socket-outlet for a particular item of equipment.

The decision as to which socket-outlets are provided with RCD protection in accordance with these criteria should be made in consultation with the client’s duty holder under the Electricity at Work Regulations 1989.

As a general principle, it may be considered that socket-outlets in commercial and industrial premises needing to have additional protection by means of an RCD include the following: those in common, circulation and public areas; those in self-catering areas; those intended for use by cleaners; and those that may reasonably be used to supply mobile equipment for use outdoors.

See decision tree

 

 

411.3.3

WNQ3

Which socket-outlets in commercial and industrial premises are NOT required to have additional protection by RCD?

 

WNA3

Socket-outlets in commercial and industrial premises must have additional protection by means of an RCD if they are rated at 20 A or less and are for general use without the supervision of a skilled or instructed person.  An exception is made for a specific labelled/identified socket-outlet for a particular item of equipment.

The decision as to which socket-outlets are provided with RCD protection in accordance with these criteria should be made in consultation with the client’s duty holder under the Electricity at Work Regulations 1989.

As a general principle, it may be considered that socket-outlets in commercial and industrial premises NOT needing to have additional protection by means of an RCD include the following: a socket-outlet labelled for the connection of a specific item of equipment; socket-outlets not intended for general use, such as those in floor service boxes intended for the connection of workstations and other IT equipment; socket-outlets for use under the supervision of skilled or instructed persons so as to minimize the possibility of careless use.

See decision tree

 

411.3.3

WNQ4

How do I decide what grade and/or type of fire alarm and emergency lighting systems should be provided for a commercial property?

 

WNA4

Reference should be to the applicable Building Regulations, BS 5839-1 and BS 5266 which give specific recommendations.

 

 

WNQ5

If an RCD is used to achieve automatic disconnection within the prescribed time, is the supplementary bonding called for in 411.3.2.6 still required?

411.3.2.2, 411.3.2.3, 411.3.2.4

WNA5

No. An RCD is a valid way of complying with automatic disconnection requirements.

 

411.4.4


 
The Electrical Safety Council and other members of the forum believe that the guidance and information contained in this section of the website is correct, but all parties must rely on their own skill and judgement when making use of it. Neither the Electrical Safety Council nor any of the other members of the forum assumes any liability to anyone for any loss or damage caused by any error or omission in this section of the website, whether such error or omission is the result of negligence or any other cause. Where reference is made to legislation, it is not to be considered as legal advice. Any and all such liability is disclaimed.

Note: Unless otherwise indicated, all references to ‘RCD’ in this section relate to residual current devices having a rated residual operating current (IΔn ) not exceeding 30 mA and an operating time not exceeding 40 ms at a residual operating current of 5 IΔn  provided as additional protection in the event of failure of the provision for basic protection and/or the provision for fault protection or carelessness by users (Regulation 415.1.1)

 

..............................................................................................................................................................................
© ESC 2008